>However, the switch failed to connect to 
  the generator and the systems ran down the batteries before the failure was 
  noticed. 
Is it just me... or does this sentence leave one to 
  believe that mayhaps the switch in question was not actually plugged into the 
  generator circuit, only the ups.? 
Generally there will be a switch which controls whether the genset is 
feeding power to the UPS or not.  If you're just testing that the generator 
is working you'd probably have that switch turned off, whilst in normal 
operation you'd have it turned on. 
Some time ago I was involved in a 
blackout in a building which we had just moved into where this switch was in the 
wrong position, and as a result we saw a similar care to what happened here (UPS 
working fine, generator working fine, but one not feeding the other) - the 
difference being that we managed to get to the switch in time and enable it 
(Kudos to the guy who ran up about 19 flights of stairs to do it!) 
Regardless of whether the switch failed, was in the wrong position, or 
anything else I can't see how this is anyones fault other than Telecoms - you 
don't run a UPS/Generator test and not actually monitor that the UPS/Generator 
are functioning correctly.  They had around 30 minutes to detect the 
problem (based on the quoted life of the batteries) which should have been 
plenty to either fix the problem (if it was just a switch in the wrong state) or 
to backout the test. 
  Scott.